I did a flow test yesterday where the municipality had recently installed a new variable speed pump at a pumping station. The static pressure was 67 psi. We flowed the hydrant and the pressure dropped to about 45 psi (flow of about 500 gpm). Then the pump kicked in and boosted the pressure back up to 65 psi at a flow of about 750 gpm. The system I am designing is a 13R, so which curve to use is obvious. However, if the sprinkler system design required 650 gpm, should I use the curve without the pump or include the new pump as the water supply for the design? Prudence may dictate that you use the supply without the pump, but what if now a pump would be required to meet that demand? I know this is rhetorical, but I'm losing sleep......

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com