It seems to meet the intent, but...... How is the closet heated? If
there is an electric heater in a storage closet, I would be very
concerned about that as a potential ignition source. If there is warm
air fed from the dwelling, it doesn't meet the standard of no
penetrations. Is the balcony protected?
At 12:56 PM 12/11/2008, you wrote:
13 R building, every residential suite having an exterior heated storage
room 5'-10" x 2'-10" with no doors or penetrations into the suite. I'd say
13R, 2002 section 6.8.6 will apply and the storage room will not be required
to be sprinklered. Any comments?
Tony