Duane,

NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and
horizontal sidewalls in relation to the wall that they are projected
from.

Sidewall sprinklers cannot be positioned in the center of a room as a
pendant.
 

Dale F. Wingard, SET
Design Manager
Triple "A" Fire Protection, Inc.
251.649.2034
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Wednesday, December 31, 2008 11:34 AM
To: [email protected]
Subject: Sidewall Sprinklers


Can a horizontal sidewall sprinkler be installed in the center of a room
(flat, smooth clg) provided sprinkler coverage is added behind the
sidewall?  In other words, not installed near a wall or soffit.

In reality a sidewall installed 4" to 6" below the ceiling (away from a
wall/soffit) should activate in similar fashion as exposed pendents and
uprights (1" - 12" below clg).  If code permits "exposed" sidewalls to
be installed below roll up doors without soffits, can't an "exposed"
sidewall be installed elsewhere?

Is there anything in the listing of a sidewall that requires the
sprinkler be installed on a wall or soffit?  Are there any ROP/ROC
responses from the committee that would help answer the question?

Thoughts?

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to