I'm not a PE nor do I play one on TV. But I've seen James' fire videos, so
I'm ahead of most plumbing designers:)

Caveats aside, I think activation depends on heat banking down from the
ceiling, and in order to get a head to throw 24' it has to go off- and
that's a long way for heat to go without a backdrop to stop heat from
continuing to the next SSP below a flat ceiling. The "wall" or soffit behind
the SW will stop that heat from continuing past it and turn it toward the
thermal element. Heat Creep?

I've never been a fan of protecting a 48' wide area by ECHSW on opposing
walls. Wouldn't think there'd be much life safety offered. 

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Monday, January 05, 2009 1:32 PM
To: [email protected]
Subject: RE: Sidewall Sprinklers

I agree, the codes do not permit installation of sidewalls without a
backwall/soffit/beam in any other situation. However, this is something I
have often wondered myself. Granted, all closed sprinklers actuated by
thermal elements require to be in proximity to a ceiling. The thermal
elements in sidewalls are the same as pendents and uprights. So why would
only sidewall also require a backwall? Is the acuation of sidewalls
different from pendents and uprights? I think the originator of this post is
asking a valid question.

Tony   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: January 5, 2009 8:55 AM
To: [email protected]
Subject: Re: Sidewall Sprinklers

The only exception to not having a wall,  soffit, or beam behind them is
when installed UNDER roll-up doors ( as allowed by 8.4.2 (3)

Roland

On Dec 31, 2008, at 11:37 AM, Dale Wingard wrote:

> Duane,
>
> NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and 
> horizontal sidewalls in relation to the wall that they are projected 
> from.
>
> Sidewall sprinklers cannot be positioned in the center of a room as a 
> pendant.
>
>
> Dale F. Wingard, SET
> Design Manager
> Triple "A" Fire Protection, Inc.
> 251.649.2034
> [email protected]
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Wednesday, December 31, 2008 11:34 AM
> To: [email protected]
> Subject: Sidewall Sprinklers
>
>
> Can a horizontal sidewall sprinkler be installed in the center of a 
> room (flat, smooth clg) provided sprinkler coverage is added behind 
> the sidewall?  In other words, not installed near a wall or soffit.
>
> In reality a sidewall installed 4" to 6" below the ceiling (away from 
> a
> wall/soffit) should activate in similar fashion as exposed pendents 
> and uprights (1" - 12" below clg).  If code permits "exposed" 
> sidewalls to be installed below roll up doors without soffits, can't 
> an "exposed"
> sidewall be installed elsewhere?
>
> Is there anything in the listing of a sidewall that requires the 
> sprinkler be installed on a wall or soffit?  Are there any ROP/ROC 
> responses from the committee that would help answer the question?
>
> Thoughts?
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Support Contractor) Office of Research 
> Services National Institutes of Health
> 301-496-0487
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to