Many OH as well as LH HSW heads and even OH Dry HSW heads are available. Reliable has MBEC-14 for those metal frame and purlin buildings, in addition to their other listings for HSW. The availability of the heads is not in question here, it's the installation, and without the wall/soffit behind the head, I know of no listing that allows the head to be installed "In Space" except for the specific exemption of NFPA 13 for under garage doors. Anyone that has the listing of such a head I'd really like to know!
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Church Sent: Monday, January 05, 2009 11:20 AM To: [email protected] Subject: RE: Sidewall Sprinklers Reliable has had a SW for EH occupancies for years, and I've looked at several projects over the years and it didn't seem to work out for any of them- but its available. Also, I believe TFP has a OH HSW, at least 5 or 6 years ago we used some of them. glc _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)