Many OH as well as LH HSW heads and even OH Dry HSW heads are available.
Reliable has MBEC-14 for those metal frame and purlin buildings, in addition
to their other listings for HSW. The availability of the heads is not in
question here, it's the installation, and without the wall/soffit behind the
head, I know of no listing that allows the head to be installed "In Space"
except for the specific exemption of NFPA 13 for under garage doors. Anyone
that has the listing of such a head I'd really like to know!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, January 05, 2009 11:20 AM
To: [email protected]
Subject: RE: Sidewall Sprinklers

Reliable has had a SW for EH occupancies for years, and I've looked at
several projects over the years and it didn't seem to work out for any of
them- but its available.

Also, I believe TFP has a OH HSW, at least 5 or 6 years ago we used some of
them.

glc