If the building is permitted to be classified 13R, the entire building is 13R. The garage being an area outside the dwelling units, will require the design criteria of 13.
Tony -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Autry, David Sent: January 7, 2009 8:30 AM To: [email protected] Subject: Apartment Building I think I know this but I want to verify. Two story apartment building on top of a parking garage. Can the garage be protected with a 13 System and the apartments on top be a 13R System? David Autry Plans Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm.ne.gov ** Note new email address: [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Joe Burtell Sent: Wednesday, January 07, 2009 9:19 AM To: [email protected] Subject: Bid Forum It's not a technical issue but does anyone have a sample bid proposal they would be willing to share. I am not looking for a worksheet to generate the numbers, more like a sheet I would send to generals with my final lump sum, inclusions, exclusions, etc... Please e-mail direct. Best regards, Joe Burtell, SET, CFPS Burtell Fire Protection Phone: 406.652.7697 Fax: 406.652.7743 Cell: 406.861.4507 Email: [email protected] Web Site: http://www.burtellfire.com P please don't print this e-mail unless you really need to _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)