The only requirement that I know of is in NFPA 14 (2003) 6.3.5.4
FDC shall be within 100 feet of a hydrant.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Medina Jr
Sent: Thursday, January 08, 2009 12:14 PM
To: [email protected]
Subject: FDC TO HYDRANT DISTANCE

Can somebody refer me to the code section that specifies the distance from the 
FDC to fire hydrant?


George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819
808-388-5974 CL#


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]