This is very similar to the discussion we had a couple of months ago, about "Outside of the dwelling unit" design in 13R, and while you'd apply 13 to the space, if it had a concealed combustible space or attic above that area, the requirements of 13 would not extend to that space.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Thursday, January 08, 2009 8:40 AM To: [email protected] Subject: Re: Apartment Building negative on that. IF it is a 13R, then the entire building is 13R and a hose stream is not required. Take a peak at the annex A.6.8.2. The TC was a tad sloppy since we had this same issue on the old wording of 6.8.2. Until said otherwise, the philosophy that the entire building must qualify as a 13R should apply and Outside the Dwelling unit is still within that building. I say IF since a garage is the main occupancy that can be separated HORIZONTALLY and be considered a separate building. Roland On Jan 8, 2009, at 5:10 AM, Todd Williams wrote: _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)