This is very similar to the discussion we had a couple of months ago, about
"Outside of the dwelling unit" design in 13R, and while you'd apply 13 to
the space, if it had a concealed combustible space or attic above that area,
the requirements of 13 would not extend to that space.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, January 08, 2009 8:40 AM
To: [email protected]
Subject: Re: Apartment Building

negative on that.  IF it is a 13R, then the entire building is 13R and a
hose stream is not required.  Take a peak at the annex A.6.8.2. The TC was a
tad sloppy since we had this same issue on the old wording of  
6.8.2.   Until said otherwise, the philosophy that the entire building  
must qualify as a 13R should apply and Outside the Dwelling unit is still
within that building.

I say IF since a garage is the main occupancy that can be separated
HORIZONTALLY and be considered a separate building.

Roland

On Jan 8, 2009, at 5:10 AM, Todd Williams wrote: