You can't just "remove" them - be serious. If pressure is over the factory setting, then a REPLACEMENT of the 300# adjustable model is available and you crank it down to 200 PSI and end the drip.
glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of douglas hicks Sent: Friday, January 23, 2009 2:42 AM To: sprinkler board Subject: pressure relief valve I was called to look a leaking riser. I got on the job site and found a Tyco Model 513 Test and Drain with a pressure relief valve. I think the pressure relief valve is leaking. The main drain outlet is wet and the sight glass is obscured with rust. Their are a total of 5 wet risers, all in a row. Some risers have pressure relief valves and some do not have pressure relief valves. Why? Can I just remove the pressure relief valve. My thought is the designer specified the pressure relief valve for a reason, the valve needs to be in place. Douglas Hicks General Fire Equipment Co of Eastern Oregon, Inc _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)