We had a similar problem with an AGF test & drain and learned that the 175 is 
real accurate.  It can start releasing pressure at around 155 to 190.  We 
replaced it with a 190 or 195 psi per their recommendation and the problem was 
solved.  I think they said the accuracy had to do with the spring and the 
concern was not so much with the lower release, but making sure the 175 was 
good.  
    Some of this could be off slightly since I am going from memory of around 
18 months ago, and we all know how memories work

 Jay Stough