I did a flow test a couple of days ago on an underground main that had recently been looped. There is a main that feeds a hydrant and sprinklers to the building at the end of the loop. I flowed the hydrant and read the pressures off the first test port on the backflow preventer (before any checks) on the system riser. The contractor called me this morning and said my test was not valid because I didn't use two hydrants, like it says in NFPA. I think I am OK and the effective point would be the connection of the main to the sprinkler system feed. Am I right or am I missing yet another obscure ruling?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com