Todd,

I have never heard of testing this way, I have always used a minimum of two
hydrants.  On a looped system if you have the manpower or water usage isn't
an issue use three hydrants taking the pressure readings from the middle
hydrant.  Do you have access to NFPA 291, this has some good diagrams for
you to use.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Friday, January 23, 2009 7:30 AM
To: [email protected]
Subject: water test location

I did a flow test a couple of days ago on an underground main that 
had recently been looped. There is a main that feeds a hydrant and 
sprinklers to the building at the end of the loop. I flowed the 
hydrant and read the pressures off the first test port on the 
backflow preventer (before any checks) on the system riser. The 
contractor called me this morning and said my test was not valid 
because I didn't use two hydrants, like it says in NFPA. I think I am 
OK and the effective point would be the connection of the main to the 
sprinkler system feed. Am I right or am I missing yet another obscure
ruling?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to