Per edition 5 of the American Mutual Insurance Alliance Simplified water
supply testing "In testing a water system at a sprinklered plant, sometimes
we can note the residual pressure from a gauge at the base of the nearest
riser. This is not recommended as standard practice, but may be used when
other methods are not practical."

The reason to flow past the "Test Gauge" is as George said, the velocity
pressure will give a lower residual than on a dead end main, where velocity
pressure will create an artificially high residual. In either case as is
often pointed out by Roland, "Does the difference between 56.017 Psi and
56.049 Psi really make a difference" when we then add a 10% or 10Psi safety
factor, and assume a relative C value for existing underground pipe.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, January 23, 2009 12:56 PM
To: [email protected]
Subject: RE: water test location

You're not affected by the velocity pressure of the water going past your
hydrant, that'd introduce errors

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, January 23, 2009 12:52 PM
To: [email protected]
Subject: RE: water test location

George,
I thought that if you did not flow past your gauge hydrant that your
residual reading would be off. Have I been wrong all these years?    