I was taught that you had to flow past your gauge hydrant to get the proper results so I would agree with the contractor. Your scenario is like a dead end main with your gauge on the last hydrant if I am interpreting it correctly.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Friday, January 23, 2009 9:30 AM To: [email protected] Subject: water test location I did a flow test a couple of days ago on an underground main that had recently been looped. There is a main that feeds a hydrant and sprinklers to the building at the end of the loop. I flowed the hydrant and read the pressures off the first test port on the backflow preventer (before any checks) on the system riser. The contractor called me this morning and said my test was not valid because I didn't use two hydrants, like it says in NFPA. I think I am OK and the effective point would be the connection of the main to the sprinkler system feed. Am I right or am I missing yet another obscure ruling? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)