I'm with George on this one.  The water doesn't care what piping
configuration is used to connect the static/residual gauge to the system -
be it a hydrant or a sprinkler riser.  The 2nd hydrant is most common
because (normally) it's the most convenient.  I've had to do exactly as you
described several times.

Ed Kramer
Littleton, CO

> 
> I did a flow test a couple of days ago on an underground main that
> had recently been looped. There is a main that feeds a hydrant and
> sprinklers to the building at the end of the loop. I flowed the
> hydrant and read the pressures off the first test port on the
> backflow preventer (before any checks) on the system riser. The
> contractor called me this morning and said my test was not valid
> because I didn't use two hydrants, like it says in NFPA. I think I am
> OK and the effective point would be the connection of the main to the
> sprinkler system feed. Am I right or am I missing yet another obscure
> ruling?
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080