I'm with George on this one. The water doesn't care what piping configuration is used to connect the static/residual gauge to the system - be it a hydrant or a sprinkler riser. The 2nd hydrant is most common because (normally) it's the most convenient. I've had to do exactly as you described several times.
Ed Kramer Littleton, CO > > I did a flow test a couple of days ago on an underground main that > had recently been looped. There is a main that feeds a hydrant and > sprinklers to the building at the end of the loop. I flowed the > hydrant and read the pressures off the first test port on the > backflow preventer (before any checks) on the system riser. The > contractor called me this morning and said my test was not valid > because I didn't use two hydrants, like it says in NFPA. I think I am > OK and the effective point would be the connection of the main to the > sprinkler system feed. Am I right or am I missing yet another obscure > ruling? > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)