That is exactly how I learned it. I didn't stay at a Holiday Inn Express, but I did sleep in my car in the parking lot. Does that count?

At 10:07 PM 1/23/2009, you wrote:
When taking the static/residual reading from a sprinkler riser, I think the
effective point (the point the calcs should be taken back to) is the point
where the non-flowing water meets the flowing water.  If the public water
main is looped, this would be where the sprinkler line ties into the public
water main.  If the public water main is dead-end and the flowing hydrant is
upstream of the sprinkler line connection, the effective point would be
where the hydrant connects.  If the flowing hydrant is connected to the
sprinkler line, the effective point would also be where the hydrant
connects.

Disregarding elevation differences, the pressure (static or residual)
throughout the non-flowing part of the piping will be the same as that at
the system riser.

Yea, I stayed at a Holiday Inn Express last night.  Anybody else?

Ed Kramer
Littleton, CO





> >Per edition 5 of the American Mutual Insurance Alliance Simplified
> water
> >supply testing "In testing a water system at a sprinklered plant,
> sometimes
> >we can note the residual pressure from a gauge at the base of the
> nearest
> >riser. This is not recommended as standard practice, but may be used
> when
> >other methods are not practical."
>
> This was taught at FM when I was there. The logic is that the
> effective point of the test would be as close to the sprinkler system
> riser as possible, which has merit to it.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to