I'd look at the spray patterns.
And consider if an attic upright (AP), or CC1, could be applied.
They have very flat patterns for their application, might be useful for that
little sliver you're trying to protect.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ryan Hinson
Sent: Monday, February 02, 2009 5:56 PM
To: [email protected]
Subject: Sprinkler protection below conveyors in pits

Where would I go to properly protect below conveyors in pits that there is
less then 4' of clear space below the return loop of the conveyor and the
conveyer belt is 60" wide with SSU's?  NFPA 13(2002) section 8.6.5 does not
address this situation in my opinion.  What is the space depth at which
sprinklers are no longer able to develop the water pattern necessary to be
practicable?

 

Thank you,

 

Ryan L. Hinson, EIT, CET, Nicet III

FP Design Manager

Fire Construction Design Services, LLC #C124

A Division of Fire Construction Services, Inc.

6950-43rd Avenue SE

St. Cloud, MN 56304

Direct:  320-250-5404 

Fax: 320-358-3495

email:   <mailto:[email protected]>
[email protected]

 

CONFIDENTIALITY NOTICE: The information contained in this message, including
any files transmitted within, is confidential, may be legally privileged,
and is intended only for the use of the individual(s) named above. The use
of any confidential or personal information may be restricted by state and
federal privacy laws.  If this message was received in error, please notify
the sender and then delete this message.

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to