This is an example of standards writing that really confuses me.  Is it a
case where BOTH conditions need to be met, or a case where any ONE condition
needs to be met?  The way condition #2 is written, it sounds as if the
intent is for any ONE condition.  I have no experience with NFPA 1142, just
my mind gone wild.

Ed Kramer
Littleton, CO

> 
> A question regarding NFPA 1142 - 4.1.5: It states "For the purpose of
> calculating minimum water supply requirements, a structure shall be
> considered an exposure hazard under the following conditions: (1) It is
> 100
> sq. ft. or larger in area and is within 50 ft. of another structure.
> (2)
> The structure, regardless of size, is of occupancy hazard classification
> 3
> or 4 as determined in Chapter 5 and is within 50 ft of another
> structure."
> 
> For the structure to be considered an EXPOSURE HAZARD it must meet both
> (1)
> & (2).  If it meets if meets just (1) and not (2), does it then fall
> under
> classification of Structure WITHOUT Exposure Hazard?
> 
> Thanks,
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> (209)334-9119