Greg, Per my understanding of the NFPA Manual of Style to require both items as a single criteria would define a multiple levels of safety situation and that is not allowed. I read this to be two separate criterion: In the first it's an exposure if it meets the two conditions-100 sqft larger and within 50 ' of another structure. In the second it is any size, classified as a 3 or 4 hazard and within 50' of another structure. If it's 99 sqft larger, not a 3 or 4 hazard but closer than 50' it's NOT a hazard. If it's 51' away and 100' sqft larger and/or class 3 or 4 it's NOT a hazard. Etc.
On Fri, Feb 6, 2009 at 8:01 AM, Gregg Fontes <[email protected]> wrote: > A question regarding NFPA 1142 - 4.1.5: It states "For the purpose of > calculating minimum water supply requirements, a structure shall be > considered an exposure hazard under the following conditions: (1) It is 100 > sq. ft. or larger in area and is within 50 ft. of another structure. (2) > The structure, regardless of size, is of occupancy hazard classification 3 > or 4 as determined in Chapter 5 and is within 50 ft of another structure." > > For the structure to be considered an EXPOSURE HAZARD it must meet both (1) > & (2). If it meets if meets just (1) and not (2), does it then fall under > classification of Structure WITHOUT Exposure Hazard? > > Thanks, > Gregg Fontes > Cen-Cal Fire Systems, Inc. > (209)334-9119 > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)