There are clear exceptions for freezer in NFPA 25 '02 12.4.3.2 and 12.4.4.2
for freezers. If this is not a freezer there is some gray in 12.4.3.2 for
pre-action and deluge that could get you to the same place.  I think because
if something could go wrong during a fire and a crafty lawyer could use what
I see is gray against you I think you should get things in writing from the
owner and AHJ if you are not doing a full trip tests.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, February 13, 2009 7:33 AM
To: [email protected]
Subject: RE: Preaction inspections

Drop the air, take off the first pce of pipe, cut in a T and valve, and full
trip to your heart's content- make it look like a freezer system.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay Stough
Sent: Friday, February 13, 2009 6:48 AM
To: [email protected]
Subject: Preaction inspections

For those of you doing inspections, how do you handle preaction systems?
13.4.3.2.3 says that they should be trip tested fully open every three years
similar to dry systems.  We don't inspect a lot of preaction systems, but
all of the owners have not let us do a full trip, they are afraid of water
leaking out of the system on to their equipment.

 Jay Stough
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to