Is it a highrise? With a little luck the 9th FLOOR could be <75' above the ground. If a HR and the zoning by floor make it a no. If it's not a HR then yes the choice of zoning is yours as the designer.
I'm not sure what a Water Source Heat Pump is. Is there a burner? Is there combustibles? Could the head be eliminated as a non-com concealed space? Brainstorming? You said there was no door that's what has me thinking in that direction. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Friday, February 13, 2009 1:48 PM To: [email protected] Subject: water source heat pumps OK gang I need some advice hopefully based on experience. We are doing an independent hotel that is being constructed more like a typical condominium. In the far end of each unit (room), there is a small enclosed closet without a door, but with a removable cover that houses a Water Source Heat Pump. I have assumed sprinkler will be required up to this point but I am open to comments on that. There is NO WAY to get concealed piping to the closet at this time. The Building is 9 Stories tall with separate FCV's on each floor etc. My Question is can I feed these closets like a shaft from the 1st floor system all of the way up in order to avoid a lot of grief and trouble to get the owner to add soffits in every Unit? All comments welcome except those that point out something painfully obvious I may be missing. Greg McGahan Operations Manager Living Water Fire Protection 1160 McKenzie Road P.O. Box 877 Cantonment, Florida 32533 (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected] _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)