We're a bit AC here, we flow the water and even throw monsters on it and
measure it, and check to see if its whats supposed to be there.

One of those things I'd rather do now than kick myself for not doing while
waiting for the bailiff to announce "All Rise".

Others could do it this way to inflate the cost, another valve, more
couplings, a cap.....

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Friday, February 13, 2009 10:37 AM
To: [email protected]
Subject: RE: Preaction inspections

Why the T Georgie?  I just cut in a valve, close it and trip the valve.

Tom Duross


There are clear exceptions for freezer in NFPA 25 '02 12.4.3.2 and 12.4.4.2
for freezers. If this is not a freezer there is some gray in 12.4.3.2 for
pre-action and deluge that could get you to the same place.  I think because
if something could go wrong during a fire and a crafty lawyer could use what
I see is gray against you I think you should get things in writing from the
owner and AHJ if you are not doing a full trip tests.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [email protected]


Drop the air, take off the first pce of pipe, cut in a T and valve, and full
trip to your heart's content- make it look like a freezer system.

glc

For those of you doing inspections, how do you handle preaction systems?
13.4.3.2.3 says that they should be trip tested fully open every three years
similar to dry systems.  We don't inspect a lot of preaction systems, but
all of the owners have not let us do a full trip, they are afraid of water
leaking out of the system on to their equipment.

 Jay Stough

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to