Also consider that when you talk about Concealed Combustible construction there are many exceptions only one of which is as follows:
8.15.1.2.9 Concealed spaces over isolated small rooms not exceeding 55 ft2 (5.1 m2) in area shall not require sprinkler protection. If you're not requiring protection over rooms 55 SF or less, this could very well be the origin of the 55 SF. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Tom Duross Sent: Friday, February 13, 2009 11:56 AM To: [email protected] Subject: RE: Sprinkler Omission Look at the committee membership. Russell, its all political. They took a standard bathroom 5' x 8' tacked on a few feet extra and said if you exceed 55 s.f. than it must be sprinklered. Dennis Briggs, Jr. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)