Did they did the spec package? Was that stated in the spec package?
IF not, send them a bill for a change order.
Roland
On Feb 25, 2009, at 3:02 PM, Fletcher, Ron wrote:
I would like the take from the PE's on forum on how to deal with a
plan
review comment from an unnamed engineering firm (RJA).
"Due to the higher than normal potential for a fire in the occupant
sleeping and common areas, the reduction in fire are (remote area) for
quick response sprinkler in accordance with NFPA #13 Figure
11.2.3.2.3.1
is not a good engineering practice. Please revise the hydraulic
calculation to account for at least the minimum 1500 square foot
design
area as specified by NFPA #13."
The hazard is a dormitory at a minimum security prison.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ