This retired PE says the unnamed engineer is wrong.  The design area
requirements are based on the degree of hazard, not the probability or
frequency of fires.

Ed Vining

On Wed, Feb 25, 2009 at 3:02 PM, Fletcher, Ron <[email protected]>wrote:

> I would like the take from the PE's on forum on how to deal with a plan
> review comment from an unnamed engineering firm (RJA).
>
> "Due to the higher than normal potential for a fire in the occupant
> sleeping and common areas, the reduction in fire are (remote area) for
> quick response sprinkler in accordance with NFPA #13 Figure 11.2.3.2.3.1
> is not a good engineering practice. Please revise the hydraulic
> calculation to account for at least the minimum 1500 square foot design
> area as specified by NFPA #13."
>
> The hazard is a dormitory at a minimum security prison.
>
> Ron Fletcher
> Aero Automatic Sprinkler
> Phoenix, AZ