Clever approach, Travis. I'll put that one in my bag-o-tricks.

Ed Kramer
Littleton, CO

 

> 2 - Increase the design area to 1500 sq ft and eliminate heads in the
> closets and washrooms from the design area per NFPA 13: 22.4.4.6.2  The
> requirements of 22.4.4.6.1 to include every sprinkler in the design area
> to
> be included in the system discharge shall not apply where the area of
> application is equal to or greater than the minimum allowable area of
> Figure
> 11.2.3.1.1 for the appropriate hazard classification (including a 30
> percent
> increase for dry pipe systems). Sprinkler discharge in closets,
> washrooms,
> and similar small compartments requiring only one sprinkler shall be
> permitted to be omitted from hydraulic calculations within the area of
> application. Sprinklers in these small compartments shall, however, be
> capable of discharging minimum densities in accordance with Figure
> 11.2.3.1.1.
> 
> I had done a job several years ago where we took the QR reduction and
> had a situation similar to what you described.  I included the heads in
> the closet and had them as 2.8K sprinklers.  However, the reviewing
> engineer required we do a minimum of 1500 sq ft.  When I took out the
> heads in the washrooms and closets, we actually had a lower demand than
> the 900 sq ft with all of the heads included.