If you saw the video James had at the AFSA convention showing heat flows ni
beamed and cathedral ceilings, you'd know why you can't put the rules in
text. HE couldn't predict which heads were going to activate first. So the
ruling in these oddballs was to seek guidance from the fire chief when he
gets done bagging groceries and is ready to out-guess what JG couldn't.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Justin Reid
Sent: Monday, March 09, 2009 10:28 PM
To: [email protected]
Subject: Re: Residential Heads under Soffit

8.10.4.1 of the 2002 edition says that residential heads are to be no  
more than four inches from the ceiling unless the listing allows  
more.Check the listing. If there is nothing in there that allows the  
deflector distance to be down to 11" then you will need sprinklers in  
the higher pocket.

The ceiling pocket exception is not listed in the code for residential  
heads. Switch to a standard or extended coverage heads instead.

Any code developers know the reason why the ceiling pocket exception  
was left out of the residential head section??? I am curious to know.


Justin D. Reid, P.E.
RLH Fire Protection
16735 Saticoy St. #110
Van Nuys, CA 91406
213-798-0251

Sent from my iPhone

On Mar 9, 2009, at 5:31 PM, George Medina Jr <[email protected]> wrote:

> I have a 500 sq. ft. room which has a soffit around the perimeter  
> that sticks out 12" and is 11" from the ceiling. My boss seems to  
> think that I can put a sprinkler under the soffit on each side of  
> the room and since the soffits are 12'-6" apart (on each side of the  
> wall) we do not have to add sprinklers in the ceiling pocket  
> (because of the 1000 cubit feet rule). Can we put a residential  
> pendent 11" from the higher ceiling (under the soffit). Are pendent  
> spacing is 16' x 16'.
>
> George Medina Jr.
> Sr. Fire Sprinkler Designer
> 95-1015 Ka'apeha Pl.
> Mililani, HI 96819
> 808-388-5974 CL#
>
>
> George Medina Jr.
> Sr. Fire Sprinkler Designer
> 95-1015 Ka'apeha Pl.
> Mililani, HI 96819
> 808-388-5974 CL#
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to