You are mixing 3 different issues.

1.  If you can maintain a 12" deflector with non-residential heads the
pocket is irrelevant.  But the 12" is complicated by the step ceiling rule a
bit.  If the res heads has a listing for 12" then the pocket is irrelevant.


2.  Pockets are only under an option for SSU/SSP and ECUP/ECP not available
in the residential category.

3.  Res heads have smaller location tolerance potentially modified by the
listing. 

Here's a question under a 36" pocket where you are using the pocket rules
how far down can the deflector be from the lower ceiling the head is in or
under?  Seems to me one could put a head up to 12" below the lower ceiling
and thus have 4' from the deflector to the top of the pocket.  In the pocket
rule the 36" is clear it's the depth of the pocket not the depth to the
head.      

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Medina
Jr
Sent: Monday, March 09, 2009 7:31 PM
To: [email protected]
Subject: Residential Heads under Soffit

I have a 500 sq. ft. room which has a soffit around the perimeter that
sticks out 12" and is 11" from the ceiling. My boss seems to think that I
can put a sprinkler under the soffit on each side of the room and since the
soffits are 12'-6" apart (on each side of the wall) we do not have to add
sprinklers in the ceiling pocket (because of the 1000 cubit feet rule). Can
we put a residential pendent 11" from the higher ceiling (under the soffit).
Are pendent spacing is 16' x 16'.

George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819
808-388-5974 CL#


George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819
808-388-5974 CL#
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to