I am not totally clear on the room size or shape.  But make sure you consult
the manufacture literature for installation guide.  Reliable for example
says perimeter obstructions less than 30" in width, a sprinkler can be the
width of drop less 8" plus the depth from sprinkler deflector to bottom of
drop away and be considered covered.  I believe you say your soffit is 11"
deep and 12" wide, so (12 -8) plus 11, if the sprinkler is 15" away your
coverage is adequate. 

Thanks
Tim Killey
Fire Busters Inc
7887 114 A St., Delta, BC
V4C 5L8
Phone 604.599.4499
Fax 604.599.4319
www.firebusters.com
email: [email protected]

 

NOTICE: The information in this email is for the intended recipient only.
Information is personal and confidential, and shall not be shared with
anyone other than the recipients of this email.  If you receive this email
in error, please contact the writer immediately.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Medina
Jr
Sent: Monday, March 09, 2009 5:31 PM
To: [email protected]
Subject: Residential Heads under Soffit

I have a 500 sq. ft. room which has a soffit around the perimeter that
sticks out 12" and is 11" from the ceiling. My boss seems to think that I
can put a sprinkler under the soffit on each side of the room and since the
soffits are 12'-6" apart (on each side of the wall) we do not have to add
sprinklers in the ceiling pocket (because of the 1000 cubit feet rule). Can
we put a residential pendent 11" from the higher ceiling (under the soffit).
Are pendent spacing is 16' x 16'.

George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819
808-388-5974 CL#


George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819
808-388-5974 CL#
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 8.0.237 / Virus Database: 270.11.7/1983 - Release Date: 03/09/09
19:20:00

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to