I am not totally clear on the room size or shape. But make sure you consult the manufacture literature for installation guide. Reliable for example says perimeter obstructions less than 30" in width, a sprinkler can be the width of drop less 8" plus the depth from sprinkler deflector to bottom of drop away and be considered covered. I believe you say your soffit is 11" deep and 12" wide, so (12 -8) plus 11, if the sprinkler is 15" away your coverage is adequate.
Thanks Tim Killey Fire Busters Inc 7887 114 A St., Delta, BC V4C 5L8 Phone 604.599.4499 Fax 604.599.4319 www.firebusters.com email: [email protected] NOTICE: The information in this email is for the intended recipient only. Information is personal and confidential, and shall not be shared with anyone other than the recipients of this email. If you receive this email in error, please contact the writer immediately. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Medina Jr Sent: Monday, March 09, 2009 5:31 PM To: [email protected] Subject: Residential Heads under Soffit I have a 500 sq. ft. room which has a soffit around the perimeter that sticks out 12" and is 11" from the ceiling. My boss seems to think that I can put a sprinkler under the soffit on each side of the room and since the soffits are 12'-6" apart (on each side of the wall) we do not have to add sprinklers in the ceiling pocket (because of the 1000 cubit feet rule). Can we put a residential pendent 11" from the higher ceiling (under the soffit). Are pendent spacing is 16' x 16'. George Medina Jr. Sr. Fire Sprinkler Designer 95-1015 Ka'apeha Pl. Mililani, HI 96819 808-388-5974 CL# George Medina Jr. Sr. Fire Sprinkler Designer 95-1015 Ka'apeha Pl. Mililani, HI 96819 808-388-5974 CL# _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - www.avg.com Version: 8.0.237 / Virus Database: 270.11.7/1983 - Release Date: 03/09/09 19:20:00 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)