If the shelves are solid and more than 64 square feet it appears in-rack
sprinklers are needed.  I do not have the 2002 edition but in 2007 NFPA 13
chapter 16, it  gives criteria for class 1 through IV commodities stored UP
TO 25 feet.  The criteria for sprinklering under every solid shelf greater
than 64 sq ft is covered in 16.1.6.2.  In addition FM data sheet 8-9 has
storage of class IV up to 10 feet in height requires 1 level of IRAS.

John Hoffman P.E. | Fire Protection Engineer | Burns & McDonnell
Engineering | 2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213

[email protected] wrote on 03/11/2009 08:39:47 AM:

> Gentlemen,
> Would you please help me?
> I have the basement in student’s dorm serving as a storage room
> approximate 2000  sqft. Around all storage room, along walls, there
> are storage racks with the solid wood  shelves (storage racks are
> about 680 sqft). The storage contains beddings: sheets,  pillows and
> comforters in the small plastic bags.
> Room is 9 ft height; first level of rack is 2 ft above floor and
> second level 5 ft above  floor. Commodities are stored to the
> ceiling of the room.
>
> Please correct me if my approach is not correct:
> 1. Storage classified as miscellaneous storage
> 2. Commodities classification: Class IV
> 3. Storage to be lower min. 18 inch from the sprinklers.
> 3. Design criteria for ceiling sprinklers based on 12.1.10 (NFPA 13
> 2002): 1500sqft/0.20  gpm/sqft
> 4. Since we have solid shelving do we need have in rack sprinklers
> and need to apply  section 12.3.1.9.2 “Where solid shelving in
> single-, double-, and multiple-row racks  exceeds 64 sqft in are or
> where the level of storage exceed 6 ft, sprinklers shall be
> installed at the ceiling and below each level of shelving”?
> It is not really clear to me that this requirement applies to
> miscellaneous storage also.
>
> I would really appreciate you help.
> Thank you,
>
> Anna Reich
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to