Thanks. That was also my understand that one level of in-rack sprinkler are needed.
What made me unsure was that when I used TYCO Sprink Code, when I plug all data with solid shelves it did not give me requirements for in-rack sprinklers. From my experience, usually it gives very good design criteria. I thought maybe I am missing some information. Way to go will be change to open racks or install one level of sprinklers? Thanks again, Anna Reich -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, March 11, 2009 3:13 PM To: [email protected] Subject: Re: Miscellaneous Storage If the shelves are solid and more than 64 square feet it appears in-rack sprinklers are needed. I do not have the 2002 edition but in 2007 NFPA 13 chapter 16, it gives criteria for class 1 through IV commodities stored UP TO 25 feet. The criteria for sprinklering under every solid shelf greater than 64 sq ft is covered in 16.1.6.2. In addition FM data sheet 8-9 has storage of class IV up to 10 feet in height requires 1 level of IRAS. John Hoffman P.E. | Fire Protection Engineer | Burns & McDonnell Engineering | 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 [email protected] wrote on 03/11/2009 08:39:47 AM: > Gentlemen, > Would you please help me? > I have the basement in student's dorm serving as a storage room > approximate 2000 sqft. Around all storage room, along walls, there > are storage racks with the solid wood shelves (storage racks are > about 680 sqft). The storage contains beddings: sheets, pillows and > comforters in the small plastic bags. > Room is 9 ft height; first level of rack is 2 ft above floor and > second level 5 ft above floor. Commodities are stored to the > ceiling of the room. > > Please correct me if my approach is not correct: > 1. Storage classified as miscellaneous storage > 2. Commodities classification: Class IV > 3. Storage to be lower min. 18 inch from the sprinklers. > 3. Design criteria for ceiling sprinklers based on 12.1.10 (NFPA 13 > 2002): 1500sqft/0.20 gpm/sqft > 4. Since we have solid shelving do we need have in rack sprinklers > and need to apply section 12.3.1.9.2 "Where solid shelving in > single-, double-, and multiple-row racks exceeds 64 sqft in are or > where the level of storage exceed 6 ft, sprinklers shall be > installed at the ceiling and below each level of shelving"? > It is not really clear to me that this requirement applies to > miscellaneous storage also. > > I would really appreciate you help. > Thank you, > > Anna Reich > > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
