Rodney,

You said you aren't hard headed and you understand the principles behind
the system pressure increases.  Here's a chance to prove both.

1.  Two containers of identical volume.  One container 50% water, the
other container 100% water.  Each has been sitting in a 50 F room with
the lid off.  In other words the liquid and the containers are at 50F. 
Now make sure the 100% container is topped off and put lids on both. 
Read the pressure gage and satisfy yourself they both read "0".  Move
both containers into a 120 F room and come back when the two systems
reach 120 F.

2.  Same as above, but remove 10% of the water from the filled container
before capping and moving.

When the systems reach 120 F, which container has the higher pressure in
each of the cases above?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to