Bill,

This is a good way to do it.  I would suggest two 12" lengths of 2" pipe
with caps on one end and a 2 to 1/4" reducer down for a pressure gauge.
Fill one half full, fill the other right up to the top, stick them in your
fridge for half a day and then thread the gauges in.  Be sure and use a
gauge you don't care about for the full pipe. %-)

Michael M. Fitz, P.E., C.F.I.
MDE Inc.
700 S. Industrial Way
Seattle, WA  98108
www.MDE.com
206-321-1804


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, March 20, 2009 2:42 PM
To: [email protected]
Subject: RE: Excessive system pressure

Rodney,

You said you aren't hard headed and you understand the principles behind
the system pressure increases.  Here's a chance to prove both.

1.  Two containers of identical volume.  One container 50% water, the
other container 100% water.  Each has been sitting in a 50 F room with
the lid off.  In other words the liquid and the containers are at 50F. 
Now make sure the 100% container is topped off and put lids on both. 
Read the pressure gage and satisfy yourself they both read "0".  Move
both containers into a 120 F room and come back when the two systems
reach 120 F.

2.  Same as above, but remove 10% of the water from the filled container
before capping and moving.

When the systems reach 120 F, which container has the higher pressure in
each of the cases above?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


__________ Information from ESET Smart Security, version of virus signature
database 3952 (20090320) __________

The message was checked by ESET Smart Security.

http://www.eset.com


 

__________ Information from ESET Smart Security, version of virus signature
database 3952 (20090320) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to