Tom, IBC 2006/903.3.1.2.1 Balconies & Decks. Note that this requirement is a subsection of 903.3.1.2 NFPA 13R sprinkler systems, so that it only applies to 13R buildings. It reads a little goofy so read it carefully. When you say to yourself, "But there's no dry head listed for 14" below anything," you'll be right. Now move on. I think it's because there have been several fires from unattended barbecues lighting up the deck above and then having the fire follow the cantilever into the floor/ceiling structure. That explains worrying about patios. I think it's in IBC instead of 13R because it was proposed by fire chief associations who got it into IBC but not NFPA. That though, is speculation.
On Wed, Mar 25, 2009 at 5:26 AM, Tom Duross <[email protected]> wrote: > I have an existing 4 sty. 13R building, sprinklered, maybe 5 years old. 2 > units/floor. IBC. > The small existing cantilevered decks (3x10) are being replaced with larger > (6x10) ones. > They're installing outside decks/balconies to the stairs off the sliders > from the living rooms. > The stairs will are open and will connect to each deck as a second/third(?) > means of egress although the stairs serve the back doors now too. > > They're asking me to install dry sidewalls to protect the decks/balconies > but I have a few questions. > 1. Do I have to also protect the stairs (existing but will connect to the > new decks) if they're open? > 2. How close to the underside of the deck overhead can I install the > sidewall? > 3. What about the top decks that aren't covered? Just place a head over it? > 4. What would you guys design this too? All heads? > I've got a stack of HVAC closets adjacent to the sliders so I think I can > run the risers there and just tee off on each floor. > One contractor has already stated a dry pipe standpipe is required, I'm not > sure about that. > > This isn't my design, just being asked to quote a sketch. > I asked how close the decks were going to be to the property line thinking > it might be a protection issue but apparently the building inspector has > signed off on the new decks providing they hire a sprinkie to put in the > heads. > > Tom > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)