Nope.  Escalators are a convenience appliance so no standpipes required
at escalator landings.  They don't count for squat in the egress plan
and are pretty much always open ...   

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Wednesday, March 25, 2009 4:36 PM
To: [email protected]
Subject: Re: side by side standpipes

So if you have a 4-story mall with escalators, you have to put a 
standpipe on each of these as well?

At 07:07 PM 3/25/2009, you wrote:
>ignoring convenient stairs as already addressed, it I certainly would
>not be the one ATTEMPTING to argue just because the design added more
>exits than minimally required I can leave out standpipes just because
>of such loose wording.  IF you provide extra exits they all are
>treated as full fledge exits and get all the bells and whistles of the
>other exits.  There is room to dance but I suggest to my members to
>keep their butts in the chairs until a better song starts.
>
>Roland
>
>On Mar 25, 2009, at 3:36 PM, Chris Cahill wrote:
>
> > Dude, the standard is clear in every required exit stair.  Even the
> > IFC uses
> > similar language.  If it ain't required you don't need a standpipe.
> > As a FF
> > I of course think that would be bad design as I would have no idea
> > when the
> > building is on fire which stairs are required and which aren't.
> > Thus I
> > wouldn't know where to find standpipes.  As an FPE I agree with
> > myself the
> > FF.  Further I'd walk from a job (in a normal economy) where the
> > standpipes
> > weren't in every stair leading to an egress.  In this economy I'd
> > certainly
> > write lotsa CYA letters for the only job we would have.  (Sorry I do
> > need to
> > eat).  As a former AHJ I'd fight for every stair until the judge
> > overruled.
> > My only case lost as AHJ was over an exterior standpipe for a
> > Cathedral
> > copper reroofing job where the Chief wanted a standpipe to reach the
> > top
> > (over 250' above grade no access from the inside).  Tactically the
> > Chief was
> > right but the City Council sided with God's representative.  Once
that
> > happened the City couldn't proceed to a judge.  I assume I'm going
> > to Hell
> > anyway so arguing against God really didn't chance anything.
> >
> > Now I can't think of a place where a stair was there but not
> > required, but
> > it is certainly theoretically possible.  (Assuming something can be
> > "certainly theoretical")  Closest comes to mind is a convenience
stair
> > connecting several floors.  Some might go to street some might not.
> >
> > In a legal contest the required part is going to be key if all the
> > experts
> > like the architect show up and have all the exiting calc's done
> > showing the
> > stair in question is not required. My money is on the NFPA committee
> > believes all stairs get standpipes but that is not what they wrote -
> > Steve.....
> >
> >
> > In a legal deposition (or worse on cross in front of the judge) on
> > the side
> > of the standpipe how are you going to answer the questions along the
> > line of
> >
> >
> > Mr. Huggins have you reviewed the Architects exiting analysis?
> >
> > Assuming you had the follow up is -
> >
> > Mr. Huggins is there anything wrong with the analysis as it applies
> > to the
> > minimum requirements of the Code?
> >
> > Assuming there wasn't -
> >
> > Mr. Huggins does the analysis show the stair in question is
required?
> >
> > And you wouldn't have gotten this far if it was required -
> >
> > Does the IFC and NFPA 14 refer to standpipes in required stairs?
> >
> > You really are in a corner to say yes -
> >
> > And finally Mr. Huggins what does the LAW say about non-required
> > stairs?
> >
> > I'd guess you'd respond "nothing, but...."
> >
> > And your counsel will have no choice but to drop the matter.
> >
> > I try to use my powers for good so let's change the IFC and NFPA 14
to
> > change this loop hole. Might be as simple as dropping the word
> > required.
> >
> > Now I don't know if Greg's stairs are required or not.  I tend to
> > think they
> > are required so really the discussion is mute but it does reveal a
> > flaw in
> > the code that until now I had not thought of.
> >
> > Chris Cahill, P.E.
> > Fire Protection Engineer
> > Sentry Fire Protection, Inc.
> >
> > 763-658-4483
> > 763-658-4921 fax
> >
> > Email: [email protected]
> >
> > Mail: P.O. Box 69
> >        Waverly, MN 55390
> >
> > Location: 4439 Hwy 12 SW
> >              Waverly, MN 55390
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
Roland
> > Huggins
> > Sent: Wednesday, March 25, 2009 4:36 PM
> > To: [email protected]
> > Subject: Re: side by side standpipes
> >
> > Just because the design exceeds the minimum number of exits needed
to
> > meet the travel distance does NOT allow you to say the extra exit is
> > not REQUIRED so no standpipe in it.  If it is an actual stairway
exit,
> > it is considered required.
> >
> > Roland
> >
> > On Mar 25, 2009, at 9:46 AM, Greg McGahan wrote:
> >
> >> This is an unusual case - it is not for volume or congestion -
there
> >> are 4 stairs, (2 sets) within 50-60 feet of each other in an
> >> amusement building. You pay to go up but you get to come down for
> >> free.
> >>
> >> My thoughts were since the hose valves are serving the same area it
> >> is overkill to calc 1,000 gpm at an elevation of only 50' - manual
> >> wet should be allowed per law, but the EOR says auto is what he
> >> wants, serving about 14,000 sqft per floor.
> >>
> >> But Ok, I got what I needed - thanks.
> >>
> >> Greg McGahan
> >> Operations Manager
> >>
> >> Living Water Fire Protection
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[email protected]
>
>To Unsubscribe, send an email
to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to