Chris:

Can show you "non-required" stairs on numerous projects.   Currently
doing a library resource center for a community college.  Three stories
with a giant open atrium - open to all three floors - right in the
center.   Grand open staircase in the center of the building - in the
language of the code, a "convenience stair".   The three required exits
are all conventional shafts and scattered around the building.   I can
show you plenty more where that one came from ...

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Wednesday, March 25, 2009 3:36 PM
To: [email protected]
Subject: RE: side by side standpipes

Dude, the standard is clear in every required exit stair.  Even the IFC
uses
similar language.  If it ain't required you don't need a standpipe.  As
a FF
I of course think that would be bad design as I would have no idea when
the
building is on fire which stairs are required and which aren't.  Thus I
wouldn't know where to find standpipes.  As an FPE I agree with myself
the
FF.  Further I'd walk from a job (in a normal economy) where the
standpipes
weren't in every stair leading to an egress.  In this economy I'd
certainly
write lotsa CYA letters for the only job we would have.  (Sorry I do
need to
eat).  As a former AHJ I'd fight for every stair until the judge
overruled.
My only case lost as AHJ was over an exterior standpipe for a Cathedral
copper reroofing job where the Chief wanted a standpipe to reach the top
(over 250' above grade no access from the inside).  Tactically the Chief
was
right but the City Council sided with God's representative.  Once that
happened the City couldn't proceed to a judge.  I assume I'm going to
Hell
anyway so arguing against God really didn't chance anything.   

Now I can't think of a place where a stair was there but not required,
but
it is certainly theoretically possible.  (Assuming something can be
"certainly theoretical")  Closest comes to mind is a convenience stair
connecting several floors.  Some might go to street some might not. 

In a legal contest the required part is going to be key if all the
experts
like the architect show up and have all the exiting calc's done showing
the
stair in question is not required. My money is on the NFPA committee
believes all stairs get standpipes but that is not what they wrote -
Steve..... 


In a legal deposition (or worse on cross in front of the judge) on the
side
of the standpipe how are you going to answer the questions along the
line of


Mr. Huggins have you reviewed the Architects exiting analysis?

Assuming you had the follow up is -  

Mr. Huggins is there anything wrong with the analysis as it applies to
the
minimum requirements of the Code?

Assuming there wasn't - 

Mr. Huggins does the analysis show the stair in question is required?

And you wouldn't have gotten this far if it was required - 

Does the IFC and NFPA 14 refer to standpipes in required stairs?

You really are in a corner to say yes -

And finally Mr. Huggins what does the LAW say about non-required stairs?

I'd guess you'd respond "nothing, but...."

And your counsel will have no choice but to drop the matter.  

I try to use my powers for good so let's change the IFC and NFPA 14 to
change this loop hole. Might be as simple as dropping the word required.


Now I don't know if Greg's stairs are required or not.  I tend to think
they
are required so really the discussion is mute but it does reveal a flaw
in
the code that until now I had not thought of.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Wednesday, March 25, 2009 4:36 PM
To: [email protected]
Subject: Re: side by side standpipes

Just because the design exceeds the minimum number of exits needed to  
meet the travel distance does NOT allow you to say the extra exit is  
not REQUIRED so no standpipe in it.  If it is an actual stairway exit,  
it is considered required.

Roland

On Mar 25, 2009, at 9:46 AM, Greg McGahan wrote:

> This is an unusual case - it is not for volume or congestion - there  
> are 4 stairs, (2 sets) within 50-60 feet of each other in an  
> amusement building. You pay to go up but you get to come down for  
> free.
>
> My thoughts were since the hose valves are serving the same area it  
> is overkill to calc 1,000 gpm at an elevation of only 50' - manual  
> wet should be allowed per law, but the EOR says auto is what he  
> wants, serving about 14,000 sqft per floor.
>
> But Ok, I got what I needed - thanks.
>
> Greg McGahan
> Operations Manager
>
> Living Water Fire Protection

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3963 (20090325) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3963 (20090325) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 