Tony:

Have been out of the office and didn't read your e-mail until this
morning.

NFPA 14, 7.3.2 and IBC 905.4 both say essentially the same thing, that
there shall be a Class I standpipe hose connection in all of the
following locations ...  and then they list the required locations.
Conspicuously, neither the code nor standard says that there shall be a
STANDPIPE at those locations, just a STANDPIPE HOSE CONNECTION.    My
take is that it is clearly within the intent of both that a single
standpipe could supply multiple hose connections at a scissor stair
condition, HOWEVER,

NFPA 14 defines a branch line as, "A piping system, generally in a
horizontal plane, connecting not more than one hose connection with a
standpipe."   So you pretty much have to supply each connection with a
dedicated 2-1/2" branch directly from the common standpipe, or it
immediately becomes a horizontal standpipe when you supply two
connections off of a single lateral pipe.   And if it were to feed three
or more connections on a given floor (even if it's a vertical riser) the
most remote standpipe demand gets boosted to 750 GPM per 7.10.1.1.2.

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 14 Technical Committee on Standpipe and
Hose Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Thursday, March 26, 2009 12:10 AM
To: [email protected]
Subject: RE: side by side standpipes

In reply to the original question, I agree with the majority. But can
you
have one common standpipe with hose connections at each stairs?

Tony 


 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3970 (20090327) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]