Of course you get the occasional AHJ that won't accept a plan because
in doesn't show the location of the deluge valve that isn't there
because you're not using one. I think the list of 44 could be
improved.

On Thu, Mar 26, 2009 at 8:21 AM, Autry, David <[email protected]> wrote:
> "CPVC is not prefabricated like steel pipe so we don't bother with the
> same level of shop drawing detail."
>
> Understood.
>
> NFPA doesn't care if it's prefabricated or not, other than to say the 
> contractor shall specify on the drawings any sections that are to be shop 
> welded and the type of fittings or formations to be used. 14.1.3 (21)
>
> Sprinkler drawings are sprinkler drawings.
>
> I never understood why I was given one-third (or less) the time for a plastic 
> job than a steel job. The requirements are the same.
>
> Maybe that's why I'm an AHJ now and not a Design Technician.
>
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
>
> ** Note new email address: [email protected]
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Fletcher, Ron
> Sent: Thursday, March 26, 2009 10:07 AM
> To: [email protected]
> Subject: RE: Does NFPA 13 require as-built drawings
>
> CPVC is not prefabricated like steel pipe so we don't bother with the
> same level of shop drawing detail.
>
> Ron Fletcher
> Aero Automatic Sprinkler
> 21605 N. Central Ave
> Phoenix, AZ 85024
> P: 623.580.7836
> F: 623.434.3420
> C: 602.763.4160
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Autry,
> David
> Sent: Thursday, March 26, 2009 8:03 AM
> To: [email protected]
> Subject: RE: Does NFPA 13 require as-built drawings
>
> Along that same line:
>
> Why is the quality of "plastic" drawings always less than "steel"
> drawings? I always fought with my bosses over this. NFPA Chapter 14
> (2002, Edition) makes has no different requirement for the two.
> Should I disapprove plastic drawings (think - cocktail napkins) that do
> not fulfill the requirements of Chapter 14?
>
> As for the as-built question: Don't send me any, I don't have the room
> or the time to deal with them.
> "Don't want 'em, Don't need 'em, Got no use for 'em"
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
>
> ** Note new email address: [email protected]
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Thursday, March 26, 2009 9:46 AM
> To: [email protected]
> Subject: RE: Does NFPA 13 require as-built drawings
>
> I'm not sure I understand.  What part of NFPA 13 says that you don't
> have to leave behind accurate system documentation?  Yes, it seems to me
> there are a few steps in this process, and sometimes it's inconvenient
> and time consuming to take all those steps, but, again, where does it
> say you leave behind something that doesn't match what you installed,
> including the AHJ approval?
>
> Maybe I'll turn this around and ask what items on the NFPA 13 working
> drawing / hydraulic calc lists have to be correct, and what items can be
> approximate and maybe corrected later on another set of documents called
> "as-builts", but only if you find a requirement to submit as-builts?
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146
> 410-544-3620 Phone
> 410-544-3032 FAX
> 412-400-6528 Cell
>
> -------- Original Message --------
> Subject: RE: Does NFPA 13 require as-built drawings
> From: <[email protected]>
> Date: Thu, March 26, 2009 10:12 am
> To: <[email protected]>
>
> You got it bucko! Con sarnt contraktors always trying to cheat the
> system out of its due! It's downright Un-American to not follow the
> plan, people got ta eat ya know! ;)
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC 29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Fletcher,
> Ron
> Sent: Thursday, March 26, 2009 10:03 AM
> To: [email protected]
> Subject: RE: Does NFPA 13 require as-built drawings
>
> So we should submit preliminary plans and get them permitted (A.22.1),
> submit working plans and get them approved (22.1.1 & A.22.1), get the
> permission of the AHJ every time we deviate from the approved working
> plan (22.1.2) and after all our deviations are approved we should submit
> the "corrected working plans" (Bill Brooks) for approval?
>
> Ron Fletcher
> Aero Automatic Sprinkler
> 21605 N. Central Ave
> Phoenix, AZ 85024
> P: 623.580.7836
> F: 623.434.3420
> C: 602.763.4160
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George
> Church
> Sent: Thursday, March 26, 2009 12:49 AM
> To: [email protected]
> Subject: RE: Does NFPA 13 require as-built drawings
>
> Then there's the contractual thing, where they make minor changes like
> the ceiling guy turns the pattern 90* or shifts it, but they don't want
> to pay you to make the change. Why should we?
>
> Glc
> Under 2002 #13 still.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
> Williams
> Sent: Wednesday, March 25, 2009 8:01 PM
> To: [email protected]
> Subject: RE: Does NFPA 13 require as-built drawings
>
> Reality check. "As-builts" are a separate document. They are usually
> generated from the original design drawing and the fitter's field notes
> (if he kept them). As to an as-built being exact - good luck.
> Contractors may keep some notes on what they change, but they are hardly
> an EXACT duplicate of what is installed (and the assumption is that the
> designer has access to them). Consequently, as-built drawings at best
> give you an idea of major changes (main and sprinkler locations) but are
> far from perfect. There is not enough money or time in any design job
> for the designer to go out and map out every piece of pipe installed.
> "If pipe lengths and fittings have changed..."? Outside of number of
> heads, what else would change? So every job would have to be re-calced.
> Also, if we have to wait for AHJ approval before any changes are made
> (22.1.2), nothing will ever get finished. In a perfect world, you are
> right, but this ain't a perfect world.
>
>
> At 07:34 PM 3/25/2009, you wrote:
>>I think the "as-built" term is a commonly used misnomer, somehow
>>distinguishing the document used to install a system from some "extra"
>>document you leave behind for the owner to use later. The proper term
>>for "as-built" should be "corrected working plan" representing the
>>completion of something that's required from the beginning. I'm not
>>saying the as-built has to be cadded up like the original. NFPA 13 is
>>silent on this. However, the drawing left behind has to be EXACTLY
> what
>>is installed, and that redlined drawing has to have the AHJ approval in
>>some manner (22.1.2). If pipe lengths or fittings have changed, then
>>"corrected hydraulic calculations" are also required. Otherwise the
>>installer has been paid but hasn't completed the job.
>>
>>Perhaps our frequent AHJ contributors could weigh in on this one as
>>well.
>>
>>Bill Brooks
>>
>>William N. Brooks, P.E.
>>Brooks Fire Protection Engineering Inc.
>>372 Wilett Drive
>>Severna Park, MD 21146
>>410-544-3620 Phone
>>410-544-3032 FAX
>>412-400-6528 Cell
>>
>>-------- Original Message --------
>>Subject: RE: Does NFPA 13 require as-built drawings
>>From: "larryshulman" <[email protected]>
>>Date: Wed, March 25, 2009 6:11 pm
>>To: <[email protected]>
>>
>>Working plans are for the installation phase, while the "as-built" set
>>is intended for use following the installation. That's why NFPA 13 is
>>silent on the as-built requirement but it appears in NFPA 25.
>>
>>I agree this appears somewhat awkward, but I suppose there's logic in
>>there somewhere. When you find it, so advise:)
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of
>>[email protected]
>>Sent: Wednesday, March 25, 2009 2:45 PM
>>To: [email protected]
>>Subject: Re: Does NFPA 13 require as-built drawings
>>
>>Okay, but NFPA 25 pertains to maintenance of systems, not installation.
>>I understand NFPA is saying: IF there are as-builts, they will be
>>stored, etc.
>>
>>Forest Wilson
>>
>>Project Manager
>>Cherokee Fire Protection Co.
>>3195 Dayton Xenia Rd Ste 900
>>Dayton OH 45434
>>
>>ph: 937-376-2333
>>fx: 614-455-4324
>>cell: 937-307-5647
>>
>>Visit our blog: _www.cherokee-fire.blogspot.com_
>>(http://www.cherokee-fire.blogspot.com/)
>>
>>
>>FIRE SPRINKLERS SAVE LIVES!!
>>
>>
>>
>>NOTICE: The information contained in this email is intended to be
> solely
>>for
>>the use of the named individual or entity to which it is directed and
>>may contain information that is privileged or otherwise confidential.
>>It is not
>>
>>intended for transmission to, or receipt by, anyone other than the
> named
>>addressee (or a person authorized to deliver it to the named
> addressee).
>>It
>>should
>>not be copied or forwarded to any unauthorized persons. If you have
>>received this electronic mail transmission in error, please delete it
>>from your system without copying or forwarding it, and notify the
>>sender of the error by reply email or by calling Cherokee Fire
>>Protection Co. at 888-347-3079 toll free.
>>
>>
>>
>>In a message dated 3/25/2009 5:44:36 P.M. Eastern Daylight Time,
>>[email protected] writes:
>>
>>Actually you'll find it in NFPA 25 as follows:
>>
>>" 12.3.2 As-built system installation drawings, original acceptance
> test
>>records, and device manufacturer's maintenance bulletins shall be
>>retained to assist in the proper care of the system and its
>>components."
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to:
>>[email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>
>>**************Great Deals on Dell 15" Laptops - Starting at $479
>>(http://pr.atwola.com/promoclk/100126575x1220635228x1201407499/aol?redi
> r=ht
> t
>>p:%2F%2Fad.doub
>>leclick.net%2Fclk%3B213153654%3B34689672%3Bo)
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to:
>>[email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to:
>>[email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to:
> [email protected]
>>
>>To Unsubscribe, send an email
> to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to