What Thom said!!

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Tuesday, April 07, 2009 3:41 PM
To: [email protected]
Subject: RE: Pipe passing thru Electrical Equipment Rooms

NFPA 70 NEVER SAYS "OTHER SYSTEMS MAY NOT BOTH ENTER AND LEAVE THE
ELECTRICAL EQUIPMENT ROOM" It only talks about the dedicated space, as we've
discussed many times. The "Show Me" always seems to become "Because I said
so" or We've always done it"

I love word searches, but I'm pretty sure that "Not" would really require a
lot of time to cover all the times it appears in a document of this size.
And "Through" is really heavy lifting too.

Proving it doesn't exist is really a pain in the butt. Maybe a committee
member of 70 could respond? If not a formal interpatation may be called for,
since this one seems to never go away.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Tuesday, April 07, 2009 1:41 PM
To: [email protected]
Subject: RE: Pipe passing thru Electrical Equipment Rooms

I understand that this spells out the areas sprinkler pipe can and can't go.
But where does it say you can or can't pass through the electrical room.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Tuesday, April 07, 2009 2:28 PM
To: [email protected]
Subject: RE: Pipe passing thru Electrical Equipment Rooms

Found it!

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Tuesday, April 07, 2009 10:33 AM
To: [email protected]
Subject: RE: Pipe passing thru Electrical Equipment Rooms

Exhibit 110-21,22,23 indicate the spaces required by 110.26(F)and show the
allowed locations of sprinkler pipe and other systems in electrical rooms.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, April 07, 2009 9:03 AM
To: [email protected]
Subject: RE: Pipe passig thru Electrical Equipment Rooms

Well he needs to re-read his NFPA 70, we reviewed this with excerpts from
the NFPA 70 Handbook which clearly describes and depicts the allowance of
the piping through the room whether it serves that room or not as long as
certain clearances were maintained.

But hey, whatever, it's his rodeo.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Tuesday, April 07, 2009 10:57 AM
To: [email protected]
Subject: RE: Pipe passig thru Electrical Equipment Rooms

Where we are, the electrical inspector does not allow us to enter in and
back out of electrical rooms. We can pipe in with pipe for sprinklers but we
can not exit out. This includes bringing UG through the floor and exiting
through a wall or ceiling. It's kinda like the roach motel - roaches check
in but they don't check out!

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, April 07, 2009 9:46 AM
To: [email protected]
Subject: RE: Pipe passig thru Electrical Equipment Rooms

The pipe is allowed to pass through the electrical room.  However there were
restricted spaces within the rooms over or in front of certain equipment
where the pipes were not permitted to be run.

Is your electrical room sprinklered?

If it is not it must meet the criteria set forth in #13 and in the Building
code otherwise it is to be sprinklered:
a. 2 hour fire-rated enclosure including protection for penetrations.
b. Only dry type electrical equipment is used.  (you need to ask, don't
assume this one) c. The room is dedicated to electrical equipment only.
d. No combustible storage is permitted to be stored in the room.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eladio N.
Alvarado
Sent: Tuesday, April 07, 2009 8:42 AM
To: [email protected]
Subject: Pipe passig thru Electrical Equipment Rooms

Forum:
I think that this subject may have been previously discussed a long time
ago, but I can't remember the final judgment, thus, the question is, how
does one justify passing pipe thru electrical or similar type rooms when its
prohibited by the NEC code? This particular installation is to meet # 13,
Light Hazard, and the local authority has no problem with it, and the rooms
have Fire Sprinklers in them, which are mandated by the locals. The
objection comes from the EOR. Help would be greatly appreciated.

Eladio Alvarado
AFSDI


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to