Well he needs to re-read his NFPA 70, we reviewed this with excerpts from the 
NFPA 70 Handbook which clearly describes and depicts the allowance of the 
piping through the room whether it serves that room or not as long as certain 
clearances were maintained.

But hey, whatever, it's his rodeo.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Tuesday, April 07, 2009 10:57 AM
To: [email protected]
Subject: RE: Pipe passig thru Electrical Equipment Rooms

Where we are, the electrical inspector does not allow us to enter in and back 
out of electrical rooms. We can pipe in with pipe for sprinklers but we can not 
exit out. This includes bringing UG through the floor and exiting through a 
wall or ceiling. It's kinda like the roach motel - roaches check in but they 
don't check out!

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, April 07, 2009 9:46 AM
To: [email protected]
Subject: RE: Pipe passig thru Electrical Equipment Rooms

The pipe is allowed to pass through the electrical room.  However there were 
restricted spaces within the rooms over or in front of certain equipment where 
the pipes were not permitted to be run.

Is your electrical room sprinklered?

If it is not it must meet the criteria set forth in #13 and in the Building 
code otherwise it is to be sprinklered:
a. 2 hour fire-rated enclosure including protection for penetrations.
b. Only dry type electrical equipment is used.  (you need to ask, don't assume 
this one) c. The room is dedicated to electrical equipment only.
d. No combustible storage is permitted to be stored in the room.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eladio N.
Alvarado
Sent: Tuesday, April 07, 2009 8:42 AM
To: [email protected]
Subject: Pipe passig thru Electrical Equipment Rooms

Forum:
I think that this subject may have been previously discussed a long time ago, 
but I can't remember the final judgment, thus, the question is, how does one 
justify passing pipe thru electrical or similar type rooms when its prohibited 
by the NEC code? This particular installation is to meet # 13, Light Hazard, 
and the local authority has no problem with it, and the rooms have Fire 
Sprinklers in them, which are mandated by the locals. The objection comes from 
the EOR. Help would be greatly appreciated.

Eladio Alvarado
AFSDI


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to