Bobby,
This is another one pf those instances where we have been told not to
"pass-thru" this room so many times we just go along to get along.I have
requested on many ocassions the chapter & verse in the electrical codes
that does not allow it but did not get it.
PLEASE make someone tell you why,other than it's a good idea.I would
like to finally know.
Lamar Vaughn
- Bobby Gillett <[email protected]> wrote:
> I understand that this spells out the areas sprinkler pipe can and can't go.
> But where does it say you can or can't pass through the electrical room.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby Gillett
> Sent: Tuesday, April 07, 2009 2:28 PM
> To: [email protected]
> Subject: RE: Pipe passing thru Electrical Equipment Rooms
>
> Found it!
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Thom McMahon
> Sent: Tuesday, April 07, 2009 10:33 AM
> To: [email protected]
> Subject: RE: Pipe passing thru Electrical Equipment Rooms
>
> Exhibit 110-21,22,23 indicate the spaces required by 110.26(F)and show the
> allowed locations of sprinkler pipe and other systems in electrical rooms.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel: 970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Tuesday, April 07, 2009 9:03 AM
> To: [email protected]
> Subject: RE: Pipe passig thru Electrical Equipment Rooms
>
> Well he needs to re-read his NFPA 70, we reviewed this with excerpts from
> the NFPA 70 Handbook which clearly describes and depicts the allowance of
> the piping through the room whether it serves that room or not as long as
> certain clearances were maintained.
>
> But hey, whatever, it's his rodeo.
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC 29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby Gillett
> Sent: Tuesday, April 07, 2009 10:57 AM
> To: [email protected]
> Subject: RE: Pipe passig thru Electrical Equipment Rooms
>
> Where we are, the electrical inspector does not allow us to enter in and
> back out of electrical rooms. We can pipe in with pipe for sprinklers but we
> can not exit out. This includes bringing UG through the floor and exiting
> through a wall or ceiling. It's kinda like the roach motel - roaches check
> in but they don't check out!
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Tuesday, April 07, 2009 9:46 AM
> To: [email protected]
> Subject: RE: Pipe passig thru Electrical Equipment Rooms
>
> The pipe is allowed to pass through the electrical room. However there were
> restricted spaces within the rooms over or in front of certain equipment
> where the pipes were not permitted to be run.
>
> Is your electrical room sprinklered?
>
> If it is not it must meet the criteria set forth in #13 and in the Building
> code otherwise it is to be sprinklered:
> a. 2 hour fire-rated enclosure including protection for penetrations.
> b. Only dry type electrical equipment is used. (you need to ask, don't
> assume this one) c. The room is dedicated to electrical equipment only.
> d. No combustible storage is permitted to be stored in the room.
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC 29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Eladio N.
> Alvarado
> Sent: Tuesday, April 07, 2009 8:42 AM
> To: [email protected]
> Subject: Pipe passig thru Electrical Equipment Rooms
>
> Forum:
> I think that this subject may have been previously discussed a long time
> ago, but I can't remember the final judgment, thus, the question is, how
> does one justify passing pipe thru electrical or similar type rooms when its
> prohibited by the NEC code? This particular installation is to meet # 13,
> Light Hazard, and the local authority has no problem with it, and the rooms
> have Fire Sprinklers in them, which are mandated by the locals. The
> objection comes from the EOR. Help would be greatly appreciated.
>
> Eladio Alvarado
> AFSDI
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)