>If I recall, the IPC has been used in the DCVA vs. RPZ debate....

Todd,

In chapter nine of the IBC, the only time the International Plumbing Code is
mentioned is with the requirement for backflow prevention. Which the water
claim jurisdiction over usually anyway.

The scope section of chapter 9 (the very beginning) only references the IFC.
I think if the IMC and IPC were to be referenced this would be the place to
do it.

Also, I do not believe a run of the mill plumbing system would need to be
tested @ 200psi for 2 hours. (Yes we have an FDC) So I'm thinking a drywall
screw in the pipe would become obvious real quick. My opinion only based on
an incident that occurred recently with us. Dry wall guys stuck a drywall
screw into a 2" CPVC elbow.

This kind of reminds me of the code official that tried to apply the area
limitations found in the alarm chapter to sprinkler systems.

Ken Holsopple
Rowe Sprinkler Systems, Inc.