Chris,
I respectfully disagree,
IFC 2006 102.7 and 102.8 can only be applied within the overall SCOPE of the
entire IFC document which is limited to Fire Suppression conditions, not
Mechanical, and not Plumbing. The Scope is found in IFC 2006 101.2
Also, according to IFC 2006 102.6 Referenced Codes and Standards,
"the codes and standards referenced in this code shall be those that
are listed in Chapter 45 and such codes and standards shall be
considered part of the requirements of this code to the prescribed extent of
each such reference."
The commentary to IFC 2206 102.6 states:
"the application of referenced standards is limited to those
portions of the standards that are specifically identified."
Please note that in IFC 2006 Chapter 45, where the reference standards and
codes are listed, IPC 2006 305.8, and IMC 2006 305.5 are NOT specifically
listed/referenced.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them?
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Friday, April 17, 2009 10:53 AM
To: [email protected]
Subject: RE: IMC, IPC and nail plates
Does our family of codes go into this level of detail? If not and I don't
think it does, the authority for the AHJ to use what Thom quoted is IFC
102.7 or IFC 102.8.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [email protected]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jeff Hewitt
Sent: Friday, April 17, 2009 10:40 AM
To: [email protected]
Subject: RE: IMC, IPC and nail plates
I think you are missing the point.
You have found the references within each Code, but do the Codes apply to
Fire Suppression piping?
Read the SCOPE of each document and you will find that it does NOT include
Fire Suppression piping.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them?
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Friday, April 17, 2009 10:28 AM
To: [email protected]
Subject: RE: IMC, IPC and nail plates
IPC 2006
305.8 Protection against physical damage. In concealed
locations where piping, other than cast-iron or galvanized steel,
is installed through holes or notches in studs, joists, rafters or
similar members less than 1.5 inches (38 mm) from the nearest
edge of the member, the pipe shall be protected by shield plates.
Protective shield plates shall be a minimum of
0.062-inch-thick (1.6 mm) steel, shall cover the area of the pipe
where the member is notched or bored, and shall extend a minimum
of 2 inches (51 mm) above sole plates and below top
plates.
IMC 2006
305.5 Protection against physical damage. In concealed
locations where piping, other than cast-iron or steel, is installed
through holes or notches in studs, joists, rafters or similar members
less than 1.5 inches (38 mm) from the nearest edge of the
member, the pipe shall be protected by shield plates. Protective
shield plates shall be a minimum of 0.062-inch-thick (1.6 mm)
steel, shall cover the area of the pipe where the member is
notched or bored, and shall extend a minimum of 2 inches (51 mm) above
sole plates and below top plates.
Here's how we deal with this.
We nail plate the sole plates(one or up to 3 depending on the construction,
houses with gypcrete floors typically have an extra plate or two depending
upon how thick the gyp is.) and slip a steel sleeve around the riser coming
thru the plate.(We find we have enough scrap pipe around to keep a constant
supply of 8" sleeves. We use 8" because we have base moldings here that go
to 10" high on occasion.)
Most walls we see are double plates at the top. Only the upper plate is the
actual "Top Plate" the second plate has a name I forget right now. Any way
we nail plate both plates and have our "Nominal" 2" below the top plate.
We've never had any problem with doing this from any inspector.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, April 17, 2009 7:59 AM
To: [email protected]
Subject: IMC, IPC and nail plates
Had an interesting encounter with an AHJ this week.
He stopped by a jobsite where we're installing CPVC in walls, and found
fault with the nail plates we're using.
I called to follow up on why he didn't like them, and asked for a code
reference. He replied even if it wasn't in the code, he'd enforce nailplates
extending further than ours as a safety issue. So I reminded him that his
authority was to enforce the PA UCC as adopted, not safety issues he took a
personal liking to.
His code reference arrived by USPS this AM. He cited the IPC and IMC as
applicable to sprinkler piping, which I disagree with.
Any thoughts or previous rulings by other AHJs?
George Church
Rowe Sprinkler
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)