that's because it doesn't exist YET. It was added to NFPA 25 at the ROP meeting. Unfortunately the ROP will not be published until June. Until then the approach to take is that the 5 yr inspection is predominately looking for evidence of excessive corrosion activity driven by MIC concerns. As identified by NFPA 13: 23.1.5.2(1), one approach for addressing MIC/unusual corrosion activity is to install corrosion resistant pipe. Since that is defined as acceptable mitigation, why inspect?
Roland On Apr 17, 2009, at 10:00 AM, Jim Johnston wrote: > Happy Friday All: > > > > Got a question regarding 5-year internal inspection on 13R CPVC > systems. I > have a system we installed back in 2003 as an exposed retro fitted > system > using CPVC, the local AHJ wants a 5-year inspection on this. > Somewhere in > the past I was told this inspection is not required for CPVC > systems, I'm > not willing to make this same statement back to the AHJ without > seeing the > code reference myself. I can't find any verbage in 2006 IFC or NFPA > 25 that > excludes CPVC from this inspection - is it in here and I'm just not > seeing > it? > > > > Jim Johnston, P.E. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
