I realize cpvc is supposed to be corrosion resistant, however 25 or the IFC
does not tie anything back to this section of 13.  IFC refers to 25, 25
say's 5-year internal inspections are required without giving a exemption
for type of pipe.  For the AHJ's on the forum what would you require?

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]

-----Original Message-----
From: Roland Huggins [mailto:[email protected]] 
Sent: Friday, April 17, 2009 10:16 AM
To: [email protected]
Subject: Re: 5 Year Inspection w/ CPVC

that's because it doesn't exist YET.  It was added to NFPA 25 at the  
ROP meeting.  Unfortunately the ROP will not be published until June.   
Until then the approach to take is that the 5 yr inspection is  
predominately looking for evidence of excessive corrosion activity  
driven by MIC concerns.  As identified by NFPA 13: 23.1.5.2(1), one  
approach for addressing MIC/unusual corrosion activity  is to install  
corrosion resistant pipe.  Since that is defined as acceptable  
mitigation, why inspect?

Roland

On Apr 17, 2009, at 10:00 AM, Jim Johnston wrote:

> Happy Friday All:
>
>
>
> Got a question regarding 5-year internal inspection on 13R CPVC  
> systems.  I
> have a system we installed back in 2003 as an exposed retro fitted  
> system
> using CPVC, the local AHJ wants a 5-year inspection on this.   
> Somewhere in
> the past I was told this inspection is not required for CPVC  
> systems, I'm
> not willing to make this same statement back to the AHJ without  
> seeing the
> code reference myself.  I can't find any verbage in 2006 IFC or NFPA  
> 25 that
> excludes CPVC from this inspection - is it in here and I'm just not  
> seeing
> it?
>
>
>
> Jim Johnston, P.E.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to