Is there no room within the freezer considering there is a 10yr inspection cycle on dry pendent sprinklers and a slightly higher cost?
The 30% increase on ALL preaction systems for storage (not occupancy hazard approach) has gone through a dance to get to ALL doing it. In the 2002 ed, you had the option of not applying a 30% increase if you could PROVE the water would discharge as quickly as a wet pipe system (under the old adage that the detection went off first so not an issue). That casual philosophy is fine for a less demanding scenario but storage can rock and roll so in 2007 it was acknowledged that we didn't really have a lot of confidence in proving the comparison and simply required ALL to have the increase. Roland On May 4, 2009, at 10:17 AM, Travis Mack, SET wrote: > We have a cold storage warehouse where the owner wants a preaction > system. > The piping will run in a heated, combustible concealed space above the > cooler/freezer. The cooler will be supplied with dry pendent > sprinklers. > There is going to be a capacity issue with this system if it is double > interlock. If we go with single interlock, doesn't the capacity > issue go > away? Because this is storage, I believe we will still need to have > the 30% > increase in design area, correct?? Also, can I grid a single > interlock > preaction system protecting a storage occupancy? > > Thanks in advance for your help. > > Travis > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)