The dry pendent sprinkler is listed as an assembly with a specific K 
factor. A regular sprinkler can be separated from the pipe and 
fittings, but the dry pendent cannot be separated from its barrel. 
That section of 13 specifically lists sprinklers by K factor only. 
Therefore, my assertion is that this could be applied.

As I inferred in my original post, I assume this is an unintended 
consequence of the way the standard is written (without test results) 
and it would probably provide protection as the standard intended. 
However, someone reviewing based on letter of the standard only would 
likely say it is not being met.



At 02:42 PM 5/4/2009, you wrote:
>Don't agree.  With that logic we couldn't put wet drops in on armovers.  The
>head is still 11.2 no matter if you connect it to sched 40 or XL or have a
>linkage mechanism in the pipe.  The only thing the cut sheet does is a
>calculation for you.  We don't know the effective diameter of the inside of
>the barrel so we really can't do this calc. It would be the equivalent of
>5.6 heads having a quick reference guide for a variety of pipe drops and
>fittings included.  Which is what we do a lot in coming up with an
>equivalent K for drops and referencing that in balancing over the 5.6 (or
>whatever k).
>
>Chris Cahill, P.E.
>Fire Protection Engineer
>Sentry Fire Protection, Inc.
>
>763-658-4483
>763-658-4921 fax
>
>Email: [email protected]
>
>Mail: P.O. Box 69
>         Waverly, MN 55390
>
>Location: 4439 Hwy 12 SW
>               Waverly, MN 55390
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Monday, May 04, 2009 1:30 PM
>To: [email protected]
>Subject: RE: Preaction: single vs double
>
>Travis,
>
>You may be opening a can of worms trying to use dry pendents in this
>area. What is your ceiling density? Section 12.1.13 (NFPA 13 2002)
>has specific K factor requirements for different densities in storage
>occupancies. With dry pendents, the K factor decreases with length of
>the head. I pulled up the Tyco DS-2 K11.2 dry pendent sprinkler as an
>example. If you have 12" of insulation and are required to be 18"
>above that, you are looking at a 30" dry pendent. The actual K factor
>for a 30" dry pendent is 10.6. That would not meet the letter of the
>requirement of 12.1.13.3. I actuality, you would probably be meeting
>the intent, but could create an issue depending on who is reviewing
>it. It would probably make more sense to change the requirement in
>NFPA 13 from K factor to orifice size, because that is in reality
>what the makes the difference.
>
>Todd
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to