Travis,

Don't forget that a cooler doesn't need a dry system or even dry pendent
sprinklers provided it doesn't freeze. The bigger the cooler the more
stable the temperature.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis
Mack, SET
Sent: Monday, May 04, 2009 10:39 AM
To: [email protected]
Subject: RE: Preaction: single vs double

Ok.  I think I found my answers already.  All preaction systems
protecting
storage can not be gridded.

7.3.2.6 System Configuration. Preaction systems of the type described in
7.3.2.1(3) and all preaction systems protecting storage occupancies,
excluding miscellaneous storage, shall not be gridded.

I can't find anything that limits my capacity.  So, the 750 gallon and
60
second trips don't come into play, but I still have the 30% penalty and
the
limit to tree or looped.  Does this sound right?

Thanks! 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis
Mack,
SET
Sent: Monday, May 04, 2009 10:17 AM
To: [email protected]
Subject: Preaction: single vs double

We have a cold storage warehouse where the owner wants a preaction
system.
The piping will run in a heated, combustible concealed space above the
cooler/freezer.  The cooler will be supplied with dry pendent
sprinklers.
There is going to be a capacity issue with this system if it is double
interlock.  If we go with single interlock, doesn't the capacity issue
go
away?  Because this is storage, I believe we will still need to have the
30%
increase in design area, correct??  Also, can I grid a single interlock
preaction system protecting a storage occupancy?
 
Thanks in advance for your help.
 
Travis
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

__________ NOD32 4052 (20090504) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to