Don't agree.  With that logic we couldn't put wet drops in on armovers.  The
head is still 11.2 no matter if you connect it to sched 40 or XL or have a
linkage mechanism in the pipe.  The only thing the cut sheet does is a
calculation for you.  We don't know the effective diameter of the inside of
the barrel so we really can't do this calc. It would be the equivalent of
5.6 heads having a quick reference guide for a variety of pipe drops and
fittings included.  Which is what we do a lot in coming up with an
equivalent K for drops and referencing that in balancing over the 5.6 (or
whatever k). 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, May 04, 2009 1:30 PM
To: [email protected]
Subject: RE: Preaction: single vs double

Travis,

You may be opening a can of worms trying to use dry pendents in this 
area. What is your ceiling density? Section 12.1.13 (NFPA 13 2002) 
has specific K factor requirements for different densities in storage 
occupancies. With dry pendents, the K factor decreases with length of 
the head. I pulled up the Tyco DS-2 K11.2 dry pendent sprinkler as an 
example. If you have 12" of insulation and are required to be 18" 
above that, you are looking at a 30" dry pendent. The actual K factor 
for a 30" dry pendent is 10.6. That would not meet the letter of the 
requirement of 12.1.13.3. I actuality, you would probably be meeting 
the intent, but could create an issue depending on who is reviewing 
it. It would probably make more sense to change the requirement in 
NFPA 13 from K factor to orifice size, because that is in reality 
what the makes the difference.

Todd