We see this with dormers, and draft stopping that was not shown. The dormers
are over framed, so we require a access opening and then treat them as
"Above and belows" as far as protection. Calc one area or the other not
both. The draft stopping we add heads to correct spacing, and extra the GC.
Usually does not affect Hyd. Calc's because they are at least 3000Sf.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, May 08, 2009 7:18 AM
To: [email protected]
Subject: wood frame attics

I am running into a situation a lot that is creating a lot of problems. I
get a set of plans for a building that has a wood truss roof and there may
be gables, dormers, changes in direction, etc. I design it based on the plan
and then when the building is built, the framers have added plywood to brace
certain elements. It does not appear on the plan and what is done is based
on how the framer ultimately normally does it, feels that day, what he has
laying around, etc. Now additional sprinklers have to be added under the
plywood (potentially significant number) and included in the remote area.
This can have a devastating impact on the hydraulics. How does everyone else
handle this?

Also, if anybody has used Tyco Attic sprinklers in this situation, how do
you determine the design area with sprinklers below a shielded area?

It's Friday and feels like Monday......

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to